Ah, you may well have something there! Well spotted, thank you!
Your eyes are definitely making some bugs shallow here...
Damon
> On 10 May 2015, at 07:49, gary.gladman at talktalk.net wrote:
>
> Hi
>
> I have been monitoring RCfH and noticed that the boiler would continue though the valve was below the Minimum Valve PC Really Open (10% - default).
>
> I noticed the following code and think it might be the cause ...
>
> OpenTRV\Arduino\V0p2_Main\FHT8V_Wireless_Rad_Valve.cpp:
>
> // Potentially accept as call for heat only if command is 0x26 (38) and value open enough as used by OpenTRV to TX.
> if((0x26 == command.command) && (command.extension >= NominalRadValve.getMinValvePcReallyOpen()))
>
> My understanding is that in the FHT8V protocol the command extension is in the range 0..255 whereas Minimum Valve PC Really Open is loosely 0..100 therefore 10(%) is compared against extension 10 which as a percentage means (10*100/255) 3% hence the boiler is being shut off significantly later than expected and with valves more closed than intended.
>
> Regards Gary
> _______________________________________________
> OpenTRV-interest mailing list
> OpenTRV-interest at lists.opentrv.org.uk
> http://lists.opentrv.org.uk/listinfo/opentrv-interest