[OpenTRV-interest] Programmable TRV performance
Damon Hart-Davis
EMAIL ADDRESS HIDDEN
Mon Feb 16 15:49:41 GMT 2015
Hi,
It may start closing well before the target temperature to try to minimise fluctuations; I start closing about 1C below the target I have in the OpenTRV control loop.
Also it may see some direct radiative heating as I sometimes do on OpenTRV units, and be reacting to that. It’s still something I’m working on handling fully elegantly.
There may also be a calibration error of +/- 1C on the temeprature sensor (the one we use are closer than that).
In other words, that place may be approaching 20C including direct radiative heat and air rising from the flow/return pipe when the valve closes thinking that it’s hit 21C.
Rgds
Damon
> On 16 Feb 2015, at 14:52, Mark Wigmore <EMAIL ADDRESS HIDDEN> wrote:
>
> Hi,
>
> Sorry if this is a bit OT, but I thought people in this forum might be the most likely to know the answer.
>
> I have a Honeywell HR25 programmable thermostat on my bedroom radiator. It is programmed for 21degC in the mornings, but I can hear the valve start closing from about 17.5deg as the room warms up and completely closed by 19deg room temperature. There's a good airgap all round the TRV; 500mm to the bed, 300mm gap under the bed, and 600mm at the end of the bed nearest the TRV. There is a window 240mm above the rad and the curtain stops 170 above.
>
> Any idea what's going on?
>
> Regards,
>
> Mark
> _______________________________________________
> OpenTRV-interest mailing list
> EMAIL ADDRESS HIDDEN
> http://lists.opentrv.org.uk/listinfo/opentrv-interest